Posted: 01/11/18 08:14pm Link  |  Quote  |  Print  |  Notify Moderator

My Onan generator runs fine with the main breaker on the generator off. Turn the breaker on and it surges in/out and will finally shut down and throw a fault code number 14 which indicates over frequency.

Any ideas what to look for?


2006 42' Allegro Bus
FMCA - F311884

GordonThree

Northern Michigan

Senior Member

Joined: 05/19/2013

View Profile


Offline
Posted: 01/11/18 11:31pm Link  |  Quote  |  Print  |  Notify Moderator

Disconnect everything you can from the other side of the main breaker, try again.

Could be a bad motor in something or a bad AC capacitor in the converter. Just grasping at troubleshooting straws here..


2013 KZ Sportsmen Classic 200, 20 ft TT
2017 Ram 2500 4x4, 6.4 HEMI, 4.10 / Auto

Ivylog

Blairsville, GA and WPB, FL.

Senior Member

Joined: 06/30/2004

View Profile


Offline
Posted: 01/12/18 05:30am Link  |  Quote  |  Print  |  Notify Moderator

I think your problem is one of the loads in your DP. Turn off all the 20 or 15 amp breakers in your 120V panel. With generator running start turning the breakers back on. Your AC/ heat pumps have a time delay so you need to wait until the compressor kicks on before going to the next breaker.


This post is my opinion (free advice). It is not intended to influence anyone's judgment nor do I advocate anyone do what I propose.

08 HR Navigator 45'
Sold 04 Dynasty after 14 great years.
How I tow.
Towing a Prius without a dolly
How I spend the winter.

RLS7201

Beautyful Downtown Gladstone, MO

Senior Member

Joined: 10/26/2002

View Profile


Offline
Posted: 01/12/18 10:29am Link  |  Quote  |  Print  |  Notify Moderator

I suspect your surging under load is lack of fuel. Could be a restricted fuel filter.

Richard


95 Bounder 32H F53
460/528 stroker
Web Master
MWPSchooners.com

Ivylog

Blairsville, GA and WPB, FL.

Senior Member

Joined: 06/30/2004

View Profile


Offline
Posted: 01/12/18 11:55am Link  |  Quote  |  Print  |  Notify Moderator

Lack of fuel is a very good recommendation and changing the fuel filter is the cheapest place to start unless it is almost new. Also, the fuel pump is a know problem area, enough so that I carry a spare one along with a filter.

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 

Open Roads Forum  >  Class A Motorhomes  >  General Topics

 > 10K diesel Onan fault code 14
Search:   Advanced Search

Search only in Class A Motorhomes


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2018 CWI, Inc. © 2018 Good Sam Enterprises, LLC. All Rights Reserved. | Terms of Use | PRIVACY POLICY | YOUR PRIVACY RIGHTS